Hi Kildarebuild. I'd say you might be confusing zones with circuits. Each room would have a separate circuit, possibly even two depending on size and distance from the manifold. A circuit is a loop from the manifold flow and return. UFH pipes have a limited max length where they must be returned to the manifold, hence the possibility of a number of circuits needed for one room. If the room is far from the manifold then the distance to the room is also part of this circuit length. I have 9 circuits and six stats downstairs approx 160 m2 all on the one zone. I set the required temp for each room or area and the actuators on the manifold open and close as required. The size of the manifold has nothing to do with the number of zones. It depends on the number of circuits and the number of circuits depends on the floor area, number of rooms, spacing of UFH pipes, heat requirement etc. I would recommend a zone for downstairs, one for upstairs and one for hot water. You would also have a manifold upstairs if using UFH. Make sure the manifold is located as centrally as possible in each floor level if possible.