...with thermally efficient floor coverings, you will only have small losses via through the sub-floor insulation as the heat generated passes easily through the floor into the room. The higher the insulation value of the floor covering, the higher the percentage of heat energy will be lost through the sub-floor insulation into the ground.
I'm more than happy to consider your calculations.Well, you calculated it! I'm saying I don't agree the calculation takes all factors fully into account.
This is a red herring. In the limit, if you heated up once from cold and left the system running forever, any additional time required would average out to zero. If you want to factor in additional heat up time, then you'll have to say how often you're proposing to switch the system on and off from cold. Then you'll also have to factor in a contribution to additional cool-down time. To be honest that's a waste of time in a broad brushstroke calculation. (If you want to propose your own numbers I can easily factor them into the calculation, but in the mean time I'm sticking to my own experience of running one of these systems for a decade, which is that additional heat-up and cool-down time are roughly equal).To get the same heat output through the floor for the length of time you want it, the heat of the slab is going to have to be increased to compensate. I don't see how your calculations factor in the additional losses from the slab to the sub-floor temperature as a result of the a higher differential for a longer time. The calculations need to be over an extended period of time rather than on losses in an instant of time.
The figures I gave for the wooden flooring include a soundproofing and moisture barrier layer for a floating installation as well as the boards themselves, which happens to be the sort of system I'm running. Having seen the sheeting go down during construction and being suprised at its thickness I very much doubt it is less insulating than a layer of glue in a fixed installation. You can check the U-values in the link I provided.The thermal resistance of the glue isn't factored in anywhere either, assuming the floor is glued to the slab. Membranes such as Elastilion will have a higher thermal resistance. Elastilions test results show their product just falling within the German guidelines for maximum thermal resistance when testing with a laminated floor panel to a combined thickness of 11.65mm (0.14 (MsqK)/W versus the max of .015).
None of the ones I checked do.There's a reason manufactures recommend UFH pipes are laid more densely where wooden floors are specified.
Not relevant to the efficiency calculation though.Another point not considered for the OP is whether the rest of the insulation and air-tightness detail is sufficient that the reduced effective 70W/square metre will meet the heat requirements for the room.
This is a red herring. In the limit, if you heated up once from cold and left the system running forever, any additional time required would average out to zero. If you want to factor in additional heat up time, then you'll have to say how often you're proposing to switch the system on and off from cold. Then you'll also have to factor in a contribution to additional cool-down time.
The increased temperature for wood flooring is between 4 and 9 degrees in all the literature I have looked at (again feel free to provide your own numbers).
... and the better end of the Kingspan range is only 40% of that (0.1 vs. 0.25 W/m²K)
Not relevant to the efficiency calculation though.
You're totally determined to miss the point, so I'll only say it one more time: that is the incremental losses for wooden floors (in response to your original statement that "it will cost you extra to run"), not the total losses. It does not exceed PassivHaus standards.If you're exceeding PassivHaus standards, then perhaps you could skip the heating altogether... and the better end of the Kingspan range is only 40% of that (0.1 vs. 0.25 W/m²K), equating to 0.4% to 1% losses.
No you didn't. Your own quote is: "One example calculation from Junckers states that the underfloor heating needs to run at 37.5 degrees in order to achieve a surface temperature of 27 at the floor." You are assuming that without the wooden surface a water temperature of 27 degrees would produce a floor surface temperature of 27 degrees. With no temperature gradient that would defy the basic laws of physics. You always have to run the water hotter than the floor temp. Your reference is nothing to do with the incremental temperature for wood.I provided a link to the Junkers specs which calculates the temp difference as 10.5 degrees for a 14mm clip system. 14mm is their thinnest product, all their others will exceed the max thermal resistance advised by the German guidelines.
Yep, I did that....you have to factor in increased losses while running at the higher temp...
And you've steadfastly not even tried to put a sensible figure on that. Remember even if you got zero additional cool-down time (which is completely alien to my own experience) the additional losses would be 10% (the fraction of heat lost through the subfloor) of the extra percentage of heat-up time. So if you want to claim significant additional losses, say even 5%, you would need 50% additional warm-up time. For instance, you'd need 12 hours extra on a 24 hour warm-up. You'd be a lot better burning your wooden floor for heat at that rate....and during the prolonged warm-up time
You're totally determined to miss the point, so I'll only say it one more time: that is the incremental losses for wooden floors (in response to your original statement that "it will cost you extra to run"), not the total losses.
It does not exceed PassivHaus standards.
No you didn't. Your own quote is: "One example calculation from Junckers states that the underfloor heating needs to run at 37.5 degrees in order to achieve a surface temperature of 27 at the floor." You are assuming that without the wooden surface a water temperature of 27 degrees would produce a floor surface temperature of 27 degrees. With no temperature gradient that would defy the basic laws of physics. You always have to run the water hotter than the floor temp. Your reference is nothing to do with the incremental temperature for wood.
And you've steadfastly not even tried to put a sensible figure on that.
My actual real-world experience with a mixture of wooden floors and porcelain tiled floors is that the rooms with wood floors reach a comfortable temperature slightly after the tiled ones