If its a standard cavity wall then its sufficient if those details are adhered to. They should be as a matter of best practice any way.
The main points to look out for are:
Jambs
Insulation at jambs behind vertical DPC... at least 25mm should be used. A much better practice is to actually fill the cavity behind the DPC with rigid insulation.. and spray foam any gaps.
Heads
Make sure Insulation is located between any concrete heads, these areas are often 'forgotten' by builders. It is usually necessary to incorporate the insulation afterwards from underneath, again i would incorporate insulation here to fill the cavity, and spray any gaps. If metal heads are used make sure they have insulation incorporated.
Cills
Make sure 25mm slip of insulation is incorporated behind the cills, before pouring the soap bar..(side note, make sure they leave enough DPC to extend up over the top of the cill and dress under window)
Thresholds (not included for some mad reason)
99.9% of time this is done incorrectly. Make sure insulation and DPC is incorporated, like a cill but reversed.