burger1979
Registered User
- Messages
- 142
the boiler should NEVER be fed from your domestic tank at all. As this leaves only a single check valve seperating your domestic water from ur system water and they can and do fail. And then ur system water would mix with domestic water!!!!!!!!!!!!
Eittyer have you plumber install a makeup tank to feed your system or better again have him seal your system completely add an expansion vessel if required (if ur boiler is a system it may not be required) and supply u with a filling loop
If the system water does get mixed with the domestic water (faulty valve now fixed) is it simply a matter of draining all the hot and cold water, (tank & cylinder) Then refilling them? The Heating system is at correct pressure, and I don't there was ever anything added to the water in the heating system. Though its probably not very clean.