Hello,
I am buying a new build house and noticed that there is no RCBO on the electric shower. There is an MCB on the shower and an RCD on the fuseboard but I thought there should be an RCBO.
Any electrician know it this is OK.
Thanks
KK
The shower circuit must be protected by an RCD, either a combined RCBO unit or a separate RCD.
If the RCD on the consumer unit is a 63amp one than it would be ok to feed the shower through it.
If you have a 40amp RCD then it's a no-no.
It is on an RCD in the consumer unit. Dont know the rating, but I, sure its OK.
Is the Main fuse on the CU rated at 63Amp? If so is there a chance it would trip/blow before the 63Amp RCD?
Tks
KK
On the Consumer unit is a couple of MCB's for scokets, Lights, cooker, shower, emmersion and Boiler. There is one RCD.
Are you saying I should have an RCD for sockets AND an RCD/MCB or RCBO for the Shower?
Because I only see 1 RCD on the board.
Thanks
KK
Bottom line is by Irish standards it is not compliant. If the property has a permanent ESB connection, they have received a cert saying the installation is compliant.
Let the builder know and give him an oppurtunity to have it rectified, on the basis that your next port of call is the ESB.