Syd, you will never get accurate information for u-vlaue on window and doors, only estimates.
I’m looking at the best cavity wall construction. I do not want to "dry line" with internal insulation. Here’s the proposed wall makup:
1. Outer wall – standard 100mm concrete block
2. Cavity 100mm with:A. Kingspan Kooltherm K8 only 60mm – U Value 0.25 or
B. Bonded Beads 100mm only - U value of 0.27 orC. Kingspan Kooltherm K8 60mm – U Value 0.25 plus 40mm Bonded Beads (beads on their own in a 40mm cavity gives U value of approx 0.57) - any ideas what the overall U value is for this combination?3. Inner wall – Quinn Lite B5 150mm block – U Value 0.17
Note: I want to use pre-fabricated concrete floors so have been recommended by Quinn to use the 150mm B5 block. Overall wall width = 350mm.
What’s the overall U value for this entire wall? Any comments and suggestions for improvement?
Hi,
I've read a thread over on boards.ie this week where one of the posters stated that he can't get any building to meet the incoming regs. unless the wall has a u-value of 0.22 or better.
Good luck
I'm no expert but I make the u-value for this wall (option A) to be 0.25.
Is there any issues with moisture through walls with
- bonded bead insulation with/without board insulation (e.g Kingspan Kooltherm K8 60mm)
- as compared to normal cavity wall (with board insulation only).
Barney, im going to completely change my opinion on pumped in insulation.. sorry....
there were some assumptions made in the above calculations that turned out to be incorrect on my part. My TC values were incorrect. Im actually going to take out the pumped in insulation calculation above....
For a regular cavity block wall 100mm, pumped in will only get you 0.3 u value.
To achieve miniumum regs (0.27) u values you need to use AAC blocks on the inner leaf of a 100 cavity.
there is one company who claims a u value of 0.2 with a 150mm cavity... but that doesnt state whether the (more expensive) AAC blocks need to be used.
My preferred cavity construction is as follows:
external render
100 dense concrete block
50 cavity
100 AAC block
100 PU board mechanically fixed
47.5 Composite plasterboard
skim finish
With this relatively easy construction you are looking at a construction u value of 0.13. There are also added advantages of having the thermal insulation within the structure which i can go into later.
if AAC blocks are used, thermal bridges are kept to a 'practical' minimal....
a TC value of 0.18 for AAC is a hell of a lot better than 1.15 for dense concrete blocks.
Ok, fair enough I missed that.
Wouldn't the lack of cavity insulation make hollowcore on the first floor a substantial cold bridge?