heinbloed said:As you said the flow and return temp.difference ( meassured at the boiler )should be around 8 degrees . To increase the efficiency of your boiler it is the best to have this difference gap as large as possible . BUT : and this is important : A difference to big could cause the screed to give off sqeeking sounds due to the higher expansion differences .It might even cause cracking , but that would be more the case with temperature differences of around 50 degrees depending on the concrete screed , hardly the case in a standard working UFH.
heinbloed said:65mm under the UFH downstairs is less then the legal min., check the SEI homepage for their min.recommendation (10cm). 25mm under the upstairs UFH is only good if you want to heat the ceiling below when turning on the heating upstairs.
. My question is: Should all the reducers be fully open when starting off this process, or should I open the reducer for the longest loop first with the other loops closed and opening them one by one?Zones pipes have different sizes . Some are fully 150 meters long , some are just 30 meters long .
So sending IN the same temperature would result in different temperatures coming OUT . This shouldn't happen .
To adjust this dilemma the " standard " for adjusting is the largest i.e. the longest pipe . This is not necessary the one from the biggest zone , it could also be an average sized zone but in a far away place in the house . The lenght of the pipe decides .
When you have found this pipe you turn the reducer fully open by turning its base , not the looking glass itself . To make as much warm water passing through the zone as possible .The little float in the reducer shows how many liters are flowing through the pipe . Read always at the lowest point of the little floating ball .
Then you go to next longest pipe . Measure the temperature at the return as described above . If it shows a larger temperature as the first one then you close the return valve ( the thing with l/min. on it with the float in it ) by turning it's base until the temperature is equal to the one you have done first .
Then you go to the third longest pipe . Again the same story . Reduce the liters per minute that pass trough the zone untill the return temperature at this zone is similar to the two return temperatures you have meassured before .
And so on untill you have reached the return of the smallest zone/shortest pipe.
All return temperatures should be the same .