hot water and central heating
Well,if the boiler is turned on for the entire year than the pump is working all the time,day and night using up electricity.Lets assume the pump uses 80 kw/h than we have 1920 watts a day,or to round up 2kw.The 80 watts difference are easily consumed by the burner,so 2 kw should be a conservative number.
2 kw a day x 180 (for a half year in the summer) would be 360 kw.Multiplied with a price of roughly €0.14 gives us a total of €50.Further we have to keep in mind that the pumps lifetime is reduced by 50% .New pump incl. labour lets say € 200,every 5 years gives a write- off of about € 40 a year.
We are at €90 for a half year of continuous warm water availability.
But that does not incl.the extra fuel that is wasted with every start of the boiler-at every start a boiler uses much more fuel as in the running modus.And we have to take into account the radiation loss of the immersion tank,which might be a gain in winter but is a nuisance during summer.Plus losses of the pipes,the boiler switches of but the pump keeps pumping the water around the system and therefore COOLS down the immersion tank.
I would calculate as a ballpark figure a Conservative €150
just for the losses,plus the costs for the fuel (oil or gas) for the warm water that you get out of the taps...
and the extras for the chimney sweeping. The chimney is cold before each boiler start and therefore condensation/soot can be a problem because it won't get really warm in the chimney during the few minutes heating up time .
Get a new boiler.One that is running only on demand .You open the tap and get warm water.You close the tap and the boiler stops.And you can dump the hot press and have a really big bathroom.And you can forget the chimney sweeper if you get a condensing boiler.
There a combi boilers available which work on gravity systems as well. Check
www.sedbuk.com