Sorry Davy, just spotted your last message. Do you think a fully sealed system would solve this problem in the long term. Boiler pressure is up about 1.2 now and the house is already starting to heat up.
Is the fully sealed system a retro fit ? Could you suggest a rough guestimate of what this might cost me ?
Davy, excellent work. I forced the red turn screw and the gushing sound and the needle shot up. I cannot beleive how simple the solution was and how much you have saved my pocket and ear ache from the good lady.
Thank you so much for all your help. I will keep an eye on the other issues and hopefully the return of pressure will have a knock on affect and solve the cold rads also. Thanks again. Where do I send payment ?