onq, what do you think of the system in the link below for the recessed problem
[broken link removed]
Well, let's see what the blurb says:
==========================================================================
Fire, Vapour & Thermal Seal Cap
for Loft Void Protection
60 minute fire rating
Ideal for use with Loft Insulation
Easy to install - pass cabling through the cover by piercing with a sharp instrument or pencil,
place over the downlight and seal with mastic. No screws or clips required
- Overcomes thermal and vapour transmission to loft voids when recessed lighting is fitted
- Eliminates condensation on roof timbers and thermal loss from living areas from warm air passing through or generated by the light fittings
- Maintains sufficient air space around the fitting to allow continuous roof insulation to be laid directly over light fittings without overheating or damage to the lighting
- Easy to fit, simply seal with general purpose mastic
- Tested and approved by the Lighting Association, helps meets building regulations as well as NHBC and other insurers' requirements
- Manufactured from inert mineral fibres which are rot, corrosion and vermin resistant
- Designed to resist the formation of water droplets
- Durable lightweight construction will not put any significant load on the ceiling
- Fire tested to BS 476 Pt.21
==========================================================================
Before I make any comments - a disclaimer:
The below is not an expert opinion nor have I tested this product or have any experience of it or read any tests on it or reviews of it.
This is just a common sense assessment by someone who has over two decades of experience of assessing materials and components and reading marketing blurb, post-qualification.
What I offer below is fair comment in the public interest and without empirical testing which may contradict what I say.
==========================
I have a difficulty accepting these claims because, as far as I know; -
- vapour transmission is unaffected by any component which fails to seal the light fitting to the ceiling.
- You can't achieve a 60 minute fire rated seal to the top face of a plasterboard ceiling using general purpose mastic.
- General purpose mastic cannot eliminate condensation on roof timbers.
- Inert mineral fibres cannot eliminate condensation on roof timbers.
- You can't achieve 60 minute rating on a cap detail if the ceiling only has 30 minutes fire resistance - the additional 30 minute rating is meaningless.
- The component is not designed to resist the formation of water droplets - they are unlikely to occur merely because the component is under a layer of insulation.
- Cannot see how the detail assists with heat dispersal, whatever about overheating - heat is contained by the detail while overheating is a condition resulting in outbreak of fire or light fitting failure.
- This detail promises nothign in relation to the overheating of the transformer, which was the only culprit in the sole instance of attic fire that I have investigated.
==========================
So I can't see all these claims being true.
While the blurb says "Fire tested to BS 476 Pt.21", this doesn't offer much in the way of assurance in and of itself.
You'd have to know the exact test and test conditions to understand what was tested and how relevant this might be to the installed detail.
Now don't get me wrong, a properly installed fire rated cover can assist in reducing fire risk.
In this case I cannot accept the claims made, particularly re; -
- the lack of any requirement to install using intumescent paste
- the lack of ventilation around the fitting and
- the lack of any strategy for the transformer.
Pass.
ONQ.
[broken link removed]
All advice on AAM is remote from the situation and cannot be relied upon as a defence or support - in and of itself - should legal action be taken.
Competent legal and building professionals should be asked to advise in Real Life with rights to inspect and issue reports on the matters at hand.