T tommied Registered User Messages 16 6 Sep 2006 #1 All, I wish to add 2 or 3 electrical sockets into my attic. I already have one socket there My question is should I use "1.5 twin and earth" or "2.5 twin and earth" for the cable ? much ta T
All, I wish to add 2 or 3 electrical sockets into my attic. I already have one socket there My question is should I use "1.5 twin and earth" or "2.5 twin and earth" for the cable ? much ta T
A Avns1s Registered User Messages 99 6 Sep 2006 #3 2.5 twin and earth PS Sorry about the Double Post. Where's the blooming delete option!? Last edited: 6 Sep 2006
B Bue5Off Registered User Messages 42 7 Sep 2006 #4 If the cables are not going to be protected in any way. I would be inclined to use 3 x 2.5sq NYM-J it is a much stronger cable than T/E and only slightly more expensive.
If the cables are not going to be protected in any way. I would be inclined to use 3 x 2.5sq NYM-J it is a much stronger cable than T/E and only slightly more expensive.