old oil boiler

Ok, firstly your 'tiger loop' should not be installed indoors, it is an outdoor model
and would be considered an increased fire risk installed internally beside a heat source.

What the heck is the green garden hose connected to???????
And as for all the tappings off in half inch? is you system microbore?

I would guess around a 70-90k btu boiler, doesn't look a whole lot bigger, but always hard to tell for sure, but as it is sporting a riello g3b (r40) burner, well this is only rated 90k btu max anyhow.

What size nozzle is installed in it? (us/gal ph)
What fuel are you using kero or gasoil?
to 90k b
 
its actually out doors,and the hose is on to a drain cock,its microbore downstairs.kero oil,
 
no, the tigerloop is installed in beside the boiler, this is no allowed, this device allows small amounts of vapor to escape which 'could' be ignited, heance they are for outdoor installation (that also means not in a boiler house or boiler cabinet)
 
Its part of its design, has to allow escape as thats how it also allows air to escape
 